IPX800 integration

Hi @cce66,

I’m replying to your message in a dedicated thread.

Thanks for your comments, I’ll be able to work on a new version :slight_smile:

Thanks @cce66 for the test and screenshots, it’s very useful!

What you see is intentional: by default, all relays arrive read-only, because a controllable relay obeys all « turn everything off » commands (scenes, Google, Alexa…) and you don’t want to accidentally turn off a pump or an HRV. To control one:

  1. Integrations → IPX800 → Configuration, field « Relays controllable by Gladys »: enter the codes, for example R1, R2 (or R1:light to make it a light), then save.
  2. Discovery tab: your relays display a « Update » button. Click on it: the functionality changes from « Status (read-only) » to a real switch.

For X-4FP zones: Off and Frost Protection work immediately; Eco and Comfort require checking « Allow Eco and Comfort from Gladys » in the Configuration.

You’re right, it’s not visible enough. In the next version, the integration will say itself when no relay is controllable, and the guide will explain it from the installation. I’m also checking your repository to verify the V5 API.

And thanks for the test proposal: having a V4 and a V5 on hand is precious, the integration had never run on a real IPX800 before. Let me know if the relays switch to a switch with these two steps.

@cce66 v0.1.2 is out: Release v0.1.2 · LM1LC3N7/gladys-ipx800 · GitHub

  • The integration status now shows how many relays are read-only, and which ones are waiting for « Update » in Discovery.
  • The guide now lists the relays to control before creating the devices: they then appear directly as switches.
  • Thanks to your repository (thank you!): outputs X-8R with a large number, like your 4784128, could not be made controllable; this is fixed. And a faulty X-THL sensor no longer publishes a measurement.

If you have time to test, here’s what would help the most:

  1. After listing R1, R2 and clicking « Update »: does the command from Gladys work in both directions? Does a change made on the IPX page appear in Gladys within about ten seconds?
  2. On your X-4FP: after Stop and Frost Protection sent from Gladys, does the IPX page only show the last mode? Does the integration status sometimes display « Unreadable Mode »?
  3. If you have an X-THL: is the temperature displayed correctly (21.5 and not 215)?
  4. On your V4: is everything found (relays, inputs, pilot wire zones)?
  5. Have the new status messages been enough for you to understand what to do?

For the V3, the Eco-Devices, and the X-Pool: they have a different API, it would be a separate integration. For the Eco-Devices, there is already GitHub - LM1LC3N7/gladys-ecodevices · GitHub if you want to try it.

for the moment it’s ok in both directions at the relay level in a quasi-immediate way (less than 1s)


for the x-thl and the x-4fp I have to reconnect them, I’ll get back to you later
following update
everything is ok for v5
for v4, I had to modify the ip and the apikey and then it commands the v4 relays (but with the v5 parameters) but they don’t find anything from v4 itself

I think we need to integrate per device to make it simpler (you can have a v5 and a v4 or even a v3 in a house)

the repository I gave you all the html with an api are autonomous devices reachable on the LAN so each with an ip (the x-thl, the x-4fp, x-4vr etc are devices connected with a cable to the ipx)
so we would need a separate integration for
ipx800 v3
ipx800 v4
ipx800 v5
ecodevices
ecodevices RT2
ecodevices ED3

The ipx 800 V5 and the ecodevices ED3 are controllable via API and MQTT
That’s it, I have the 6 devices available for testing at the moment

Thank you @cce66, great feedback! I’m glad that the V5 relays respond in both directions.

For V4, you found a real issue. When you changed the address and key in the configuration, the devices created for V5 (R1, R2…) started controlling the V4 relays. For integration, « R1 » was just « relay 1 », without knowing which box. So, your « Controllable Relays » list from V5 was applied to V4. And Discovery didn’t show anything new: the V4 relays had the same names as those from V5, already created.

This is fixed in v0.1.3: Release v0.1.3 · LM1LC3N7/gladys-ipx800 · GitHub

What’s new:

  • Each IPX800 keeps its devices. The integration remembers which box they belong to: V5 by its MAC address, V4 by its address. If another IPX800 responds, its devices won’t send anything to it, not even a « turn everything off ». The status tells you what’s happening.
  • Up to three IPX800s in a single integration. No need for an integration per model: the configuration now has blocks « IPX800 #2 » and « IPX800 #3 ». Each has its model, address, key, and list of controllable relays.
  • The wrong model is detected. If you choose « V5 » for a V4 (or vice versa), the status and the « Test Connection » button will tell you.
  • Discovery no longer keeps devices from a box that is no longer read (your test with the fake address). It clears until the IPX800 responds.

To upgrade to v0.1.3 with your V5 and V4, in this order:

  1. Before updating, put the V5 back in the top fields: V5 model, its address, its key. Save. The old version only remembered the last IPX800 read: that’s why it needs to be your V5.
  2. Update the integration.
  3. The status will say that your devices are from the old version and that the IPX800 read is your V5, with the end of its MAC address. This is normal: the old version didn’t note their box, you need to confirm it once. Until then, only Off and Frost Protection work; turning on is refused.
  4. In the configuration, click twice « Reattach Devices » (IPX800 #1), within a minute. Everything starts up again, with your scenes.
  5. In « IPX800 #2 », put the V4: V4 model, its address (add :port only if it’s not 80), its API key, and its controllable relays (e.g., R1). If it has extensions, list them in « IPX800 #2 (V4) Extensions » (e.g., FP1-FP4). Save.
  6. In Discovery, the V4 devices arrive under the name « IPX800 #2 · Relay 1 (R1) ». The status shows both IPX800s in a single block, separated by « | » (« IPX800 #1: … | IPX800 #2: … »).

If you have already updated with the V4 on top, the status will tell you that the IPX800 read is the V4. Do not click « Reattach » in this case. Instead, do this:

  • if, with the old version and the V4 on top, you created other devices (R3, an input D2, a zone FP…), delete them first: otherwise they would go to the V5 when reattaching. You will recreate those from the V4 from « IPX800 #2 » in step 6;
  • put the V5 back on top (V5 model, its address, its key) and save. The status will name your V5 with the end of its MAC address. This time, nothing is sent to your devices, not even Off or Frost Protection, because the old version read the V4 in this place;
  • click twice « Reattach Devices » (IPX800 #1), within a minute: everything starts up again;
  • then do steps 5 and 6.

In the future, to try another box, don’t replace the V5 address: add it as #2 or #3.

For V3, Eco-Devices RT2, and ED3: these are three new integrations, published today. I’ll put my questions just below.

When you have tested the new version, two things would help me:

  • which model you had put the V4 in during your test (V4 or V5);
  • what http://<ip-de-ta-V5>/api/system/info?ApiKey=… (just the field names, without the key or the full MAC address).

And the X-THL and the X-4FP, when you can!

@cce66 the three other integrations you proposed to test are published: IPX800 V3, Eco-Devices RT2 and Eco-Devices ED3 (details in post #436 of the integrations thread). Thanks again for your submission, it was used for all three.

Since none of them have yet run on a real device, here’s what would help the most. For raw responses, open the address in a browser and copy the text (remove your API key if there is one).

IPX800 V3

  1. The content of http://<ipx>/globalstatus.xml (or /status.xml if the first one doesn’t exist).
  2. With manually typed addresses, not with your Api-Deck (its « Preset sortie » sends the list index, so « 1 - On » gives set1=0): http://<ipx>/preset.htm?set1=1 then ?set1=0 on a relay you can see. Does the first one turn it on and the second one turn it off? And on a relay in pulse mode?
  3. Right after reconnecting the IPX: does globalstatus.xml respond for a moment with all analog values at 0 and <dnsstatus>pending</dnsstatus>? And if it doesn’t have Internet access, does it stay like that?

Eco-Devices RT2
4. The responses of http://<rt2>/api/xdevices.json?key=…&Get=R and …&Index=all. I especially need to know if "product": "EcoDevices_RT" is in each response (otherwise the integration does nothing), and in what unit are the teleinfo and clamp indexes (Wh or kWh): compare with the index of your meter and the Eco-Devices page. As long as this isn’t confirmed, these indexes aren’t offered.
5. With your X-4FP: the exact texts of the modes in Get=FP.

Eco-Devices ED3
6. The response of http://<ed3>/api/system/info?ApiKey=…: is there a MAC address?
7. For a teleinfo meter, and for a meter powered by a clamp: the index value of /api/object/core_logger?option=filter_state next to what the ED3 page displays. The GCE example suggests that the clamps are in mWh, not Wh; as long as this isn’t confirmed, these meters aren’t offered.
8. To control an X-8R output: in x8r/<n>/SetOnR, is <n> the position in the list (0) or the _id (4259840)? In the meantime, these outputs remain read-only.

No need to do everything at once: even one or two responses help move things forward.

Hi @lmilcent

For V3 I need to rewire it

IPX800 V5
http://192.168.1.120/api/system/info?ApiKey=apikey-IPX800V5
{
  "productName": "IPX800_V5",
  "familyDevice": "X-Devices",
  "macAdress": "XX-XX-A3-05-XX-XX",
  "hostName": "IPX800V5A",
  "firmwareVersion": "5.7.2",
  "compiled": "May 19 2026 15:46:10"
}
Eco-Devices RT2
KWH teleinfo unit, W clamp unit
http://192.168.1.231/api/xdevices.json?key=apikey-rt2&Get=R
{
    "product": "EcoDevices_RT",
    "status": "Success",
    "R1": 0,
    "R2": 0,
    "R3": 0,
    "R4": 0,
    "R5": 0,
    "R6": 0,
    "R7": 0,
    "R8": 0,
    "R9": 0,
    "R10": 0
}

http://192.168.1.231/api/xdevices.json?key=apikey-rt2&Index=all
{
    "product": "EcoDevices_RT",
    "status": "Success",
    "Index_C1": 149399,
    "Index_C2": 0,
    "Index_C3": 0,
    "Index_C4": 0,
    "Index_C5": 0,
    "Index_C6": 0,
    "Index_C7": 0,
    "Index_C8": 0,
    "Index_C9": 0,
    "Index_C10": 0,
    "Index_C11": 0,
    "Index_C12": 0,
    "Index_TORE1": 271232,
    "Index_TORE2": 660664,
    "Index_TORE3": 1654075,
    "Index_TORE4": 0,
    "Index_TORE5": 0,
    "Index_TORE6": 0,
    "Index_TORE7": 0,
    "Index_TORE8": 0,
    "Index_TORE9": 0,
    "Index_TORE10": 0,
    "Index_TORE11": 0,
    "Index_TORE12": 0,
    "Index_TORE13": 0,
    "Index_TORE14": 0,
    "Index_TORE15": 0,
    "Index_TORE16": 0,
    "Index_TORE17": 1846258,
    "Index_TORE18": 8331781,
    "Index_TORE19": 0,
    "Index_TORE20": 227258,
    "Index_TI1": 132533718,
    "Index_TI2": 0,
    "Index_TI3": 4294967295,
    "Index_TI4": 4294967295,
    "Index_TI5": 4294967295,
    "Index_TI6": 4294967295,
    "Index_TI7": 4294967295
}

http://192.168.1.231/api/xdevices.json?key=apikey-rt2&Get=FP
{
    "product": "EcoDevices_RT",
    "status": "Success",
    "FP1 Zone 1": 0,
    "FP1 Zone 2": 0,
    "FP1 Zone 3": 0,
    "FP1 Zone 4": 0,
    "FP2 Zone 1": 0,
    "FP2 Zone 2": 0,
    "FP2 Zone 3": 0,
    "FP2 Zone 4": 0
}

Eco-Devices ED3
http://192.168.1.162/api/system/info?ApiKey=apikey-EDRT3
{
  "productName": "ECODEVICES3",
  "familyDevice": "X-Devices",
  "macAdress": "XX-X4-X3-31-X1-X8",   OUI MAC address
  "hostName": "ECODEVICES3",
  "firmwareVersion": "1.3.0 ",
  "compiled": "Aug 20 2026 14:51:29"
}
http://192.168.1.162/api/object/core_logger?option=filter_state?ApiKey=apikey-EDRT3
[{"_id":851968,"index":132533861,"indexprix":96058,"moyenne":811,"instMax":3180,"instMin":570,"tarif":0},{"_id":851969,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851970,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851971,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851972,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851973,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851974,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851975,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851976,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851977,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851978,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851979,"index":3293592,"indexprix":56101,"moyenne":585,"instMax":3066,"instMin":330,"tarif":0},{"_id":851980,"index":1064294,"indexprix":18029,"moyenne":11,"instMax":48,"instMin":0,"tarif":0},{"_id":851981,"index":1475571,"indexprix":24210,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851982,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851983,"index":1063454,"indexprix":18014,"moyenne":9,"instMax":34,"instMin":0,"tarif":0},{"_id":851984,"index":131571,"indexprix":2429,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851985,"index":1172,"indexprix":8,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851987,"index":122117,"indexprix":131,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851988,"index":439831,"indexprix":7396,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851990,"index":19610,"indexprix":249,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851991,"index":274442,"indexprix":4715,"moyenne":57,"instMax":75,"instMin":0,"tarif":0},{"_id":851993,"index":60707000,"indexprix":17067,"moyenne":0,"instMax":0,"instMin":0,"tarif":0},{"_id":851994,"index":0,"indexprix":0,"moyenne":0,"instMax":0,"instMin":0,"tarif":0}]"average":0,"instMax":0,"instMin":0,"tariff":0},{"_id":851996,"index":0,"indexprice":0,"average":0,"instMax":0,"instMin":0,"tariff":0},{"_id":851997,"index":0,"indexprice":0,"average":0,"instMax":0,"instMin":0,"tariff":0}]

Clamps in mA display in W
For the X8-R I have to reconnect it

On the ECO RT2 integration side, it sees 10 relays, 12 inputs
On the IPX800 side, I think having an integration by category will be simpler for the user and easier for code maintenance. Moreover, these three IPX V3 V4 V5 have different designs in terms of features (they have a scenario engine, advanced home automation capabilities, email and push notifications, etc., but they are frozen)

Thanks @cce66 for all these readings, they have been very helpful!

What has changed thanks to you (Eco-Devices RT2 0.1.2 and ED3 0.1.2, released today; they will arrive in the store at the next indexer update):

  • Téléinfo in Wh, confirmed. Your RT2 and ED3 read the same Linky: 132 533 718 on one side, 132 533 861 on the other, a few minutes later. The page displays kWh, but the API gives Wh. On the RT2, the Téléinfo is now offered in Discovery and published in kWh (it was waiting for your response).
  • RT2: Missing Téléinfo entries (the value 4294967295 on TI3 to TI7) are never published.
  • RT2: The clamps are read up to the 20 (you have them on 17, 18, and 20), but not yet offered: a comparison with the page is missing (question 1).
  • RT2: The pilot wire responds 0 everywhere at your place. These areas remain read-only: Stop and Anti-freeze still work; Eco and Comfort are refused as soon as the area has been read with this 0, until we know what it means.
  • ED3: The MAC address is correctly read (the ED3 is recognized by it), the meters are correctly recognized even when some are missing from the list, and water is published in m³.

IPX800: An integration per model? I agree with you in principle, and it’s already almost the case: an integration per family of devices that speak the same API. IPX800 V3, original Eco-Devices, RT2, and ED3 each have their own. Only the V4 and V5 are together because they do the same thing (relays, inputs, X-4FP, X-THL) with two similar APIs. I prefer not to separate them now: you just upgraded to 0.1.3, and a separation would force you to start over (devices, scenes). In each integration, we keep the possibility of having up to three boxes of the same model: it doesn’t bother those who only have one.

What would still help me (remove your API key, as last time):

Eco-Devices RT2

  1. Clamps: at the same time, what is the value of Index_TORE1 in the API, and what does the Eco-Devices page show for clamp 1 (with the unit)? And clamps 17 to 20: are these other clamps, or the production of clamps 1 to 4?
  2. Pilot wire: do you have an X-4FP connected to the RT2? If yes, change the mode of a zone from the Eco-Devices page, then send …&Get=FP: does the 0 change?
  3. The response of …&Get=D, and …&Get=XTHL if you have an X-THL.
  4. The firmware version of the RT2.

Eco-Devices ED3
5. The complete response of http://<ED3>/api/object/ed3/0?ApiKey=…, especially ID_Logger_tore and ToreName: it tells which meters come from your clamps.
6. For meter 11 (index 3 293 592): what value does the ED3 page display, and in what unit?
7. Meter 25 (index 60 707 000): is this your water? Does your water meter display approximately 60.7 m³ (or a fixed difference)?
8. When the X-8R is reconnected: the response of …/api/ebx/x8r?ApiKey=….

No need to do everything at once: even one or two answers help move forward. For the V3, when you have rewired it, question 6 still applies.

Thanks again!

Which elements are pending
index_tore1=total consumption on torus 1
on the page we have the power consumed at time T
clamps 1 to 16
clamps 17 to 20 and beyond (remainder when there was an x400 CT extension wired to it)
2. not at the moment, I’m going to wire one
3. same
4. version 3.00.04
5.

http://192.168.1.162/api/object/ed3?ApiKey=apikey-EDRT3
{
  "_id": 1245184,
  "name": "ED3",
  "errorStatus": "0x0000",
  "ID_Logger_tore": [
    851979,
    0,
    0,
    851982,
    0,
    851988,
    851990,
    851984
  ],
  "ID_Logger_tore_neg": [
    851987,
    851980,
    851981,
    0,
    851983,
    851985,
    851991,
    0
  ],
  "ConsoTore": [
    50,
    50,
    20,
    50,
    50,
    20,
    20,
    20
  ],
  "ToreName": [
    "T1-EDF",
    "T2-Maison",
    "T3-Piscine",
    "T4-Load",
    "T5-Grid",
    "T6-Solaire",
    "T7-Batterie +",
    "T8-Batterie -"
  ],
  "ID_Logger_pulse": [
    851993,
    851994,
    851996,
    851997
  ],
  "ConsoPulse": [
    1000,
    1,
    1000000,
    1
  ],
  "PulseName": [
    "Eau",
    "Pulse 2",
    "Tri",
    "Pulse 4"
  ],
  "RelayName": [
    "Relay 1",
    "Relay 2"
  ],
  "RelayMemoryMode": true,
  "refPowerFactor": 0,
  "Relay_state": [
    false,
    false
  ],
  "Relay_command": [
    false,
    false
  ],
  "Pulse_state": [
    false,
    false,
    false,
    false
  ],
  "Pulse_cpt": [
    0,
    0,
    0,
    0
  ],
  "Pulse_inst": [
    0,
    0,
    0,
    0
  ],
  "Pulse_conso": [
    0,
    0,
    0,
    0
  ],
  "powerFactor": 66.65819,
  "cosphi": [
    93.94736,
    5.895676,
    0,
    0,
    5.707409,
    0,
    52.18113,
    53.8461
  ],
  "irms": [
    "6580",
    "-947",
    "0",
    "0",
    "-939",
    "0",
    "-519",
    "-528"
  ],
  "conso": [
    0,
    0,
    0,
    0,
    0,
    0,
    0,
    857
  ],
  "puissance": [
    1455467,
    -13160,
    0,
    0,
    -12625,
    0,
    -63810,
    -67039
  ],
  "urms": 235.5297
}
http://192.168.1.162/api/object/ed3/0?option=filter_state&ApiKey=apikey-EDRT3
{
  "_id": 1245184,
  "Relay_state": [
    false,
    false
  ],
  "Relay_command": [
    false,
    false
  ],
  "Pulse_state": [
    false,
    false,
    false,
    false
  ],
  "Pulse_cpt": [
    0,
    0,
    0,
    0
  ],
  "Pulse_inst": [
    0,
    0,
    0,
   0
  ],
  "Pulse_conso": [
    0,
    0,
    0,
    0
  ],
  "powerFactor": 54.09643,
  "cosphi": [
    60.95095,
    6.054193,
    0,
    0,
    4.773418,
    0,
    53.19096,
    48.14738
  ],
  "irms": [
    "2570",
    "-953",
    "0",
    "0",
    "-971",
    "0",
    "-504",
    "-542"
  ],
  "conso": [
    0,
    0,
    0,
    0,
    0,
    0,
    0,
    858
  ],
  "puissance": [
    371970,
    -13701,
    0,
    0,
    -11010,
    0,
    -63782,
    -62032
  ],
  "urms": 237.4558
}
http://192.168.1.161/api/object/ed3/0?option=objDescriptor&ApiKey=apikey-EDRT3
{
  "_id": 1245184,
  "status": 237,
  "IN1": 0,
  "IN2": 0,
  "IN3": 0,
  "IN4": 0,
  "R1": 0,
  "R2": 0,
  "TORE1": 354,
  "TORE2": 24,
  "TORE3": 0,
  "TORE4": 0,
  "TORE5": 7,
  "TORE6": 0,
  "TORE7": 66,
  "TORE8": 65,
  "instPost1": 600,
  "instPost2": 0,
  "instPost3": 66,
  "instPost4": 0,
  "indexPost1": 132584173,
  "indexPost2": 449339,
  "indexPost3": 278471,
  "indexPost4": 61503000,
  "instTotal1": 0,
  "instTotal2": 0,
  "instTotal3": 0,
  "instTotal4": 59,
  "instTotal5": 610,
  "indexTotal1": 449339,
  "indexTotal2": 126533,
  "indexTotal3": 19610,
  "indexTotal4": 278471,
  "indexTotal5": 132584173
}
  1. 61503.0 L currently for water

there you go

Thanks @cce66, the complete configuration of the ED3 has unlocked everything!

Eco-Devices ED3 0.2.0 (Release v0.2.0 · LM1LC3N7/gladys-ecodevices-ed3 · GitHub)

  • Your clamps are offered in Discovery, with their names: « T1-EDF · Consumption (C11) », « T6-Solar… », « Water · Water (C25) »… The integration links each meter to its clamp (positive and negative direction) or to its pulse input via ID_Logger_tore, ID_Logger_tore_neg, and ID_Logger_pulse.
  • Clamp unit: Wh, confirmed by your readings. Between your #7 and #9 (71 h), the meter of T7 (negative direction) recorded 4,029, which is an average of 57 W, and T7 was measuring exactly around 60 W at both times. They are published in kWh.
  • Instantaneous power per clamp, in W: the ED3 provides it in mW (for T1: 6.58 A × 235.5 V × cos φ 0.94 ≈ 1,455 W, the ED3 says 1,455,467). The sign follows the clamp direction: positive towards its main meter, negative towards its « negative » meter.
  • Water in liters, confirmed: 61,503,000 on the ED3 side for 61,503.0 L on your meter. It is published in m³.

To see them: Discovery tab, then « Update » on your ED3. The already created meters keep their values: no jump in the history.

Eco-Devices RT2 0.1.3 (Release v0.1.3 · LM1LC3N7/gladys-ecodevices-rt2 · GitHub)

  • Clamps 17 to 20 (the rest of your old X400 CT) are no longer read.
  • Clamps 1 to 16 are still not offered: the RT2 does not provide the unit of Index_TORE anywhere, and its page only displays the power. I prefer not to publish anything rather than a false energy index, which would remain forever in Gladys’ history (see question 1).
  • Pilot wire: as long as a zone responds with a number instead of a mode, Eco and Comfort are refused; Stop and Frost protection still work.
  • Your firmware 3.00.04 is noted as tested (for reading).

If you have a moment:

RT2

  1. For the clamp unit: two readings of …&Index=all about an hour apart, noting the time, with a stable power device alone on a clamp (e.g., a 1,500 W heater), or the average power of the clamp on the page during that hour. A difference of about 1,500 will mean Wh.
  2. When the X-4FP is wired: the response of …&Get=FP, then the same after changing the mode of a zone from the Eco-Devices page (text or number?).

ED3
3. The objDescriptor came from 192.168.1.161 and the rest from .162: is it the same ED3 (typo) or two devices?
4. T8 « Battery - » measures -67 W but has no negative meter, and it’s the only clamp where conso is not 0 (857). Is it connected as you want, and does conso increase over time?
5. « Sort » (pulse 3, connected to meter 28, which is a gas meter in the GCE table): which meter is this for you?
6. Do the names offered in Discovery seem clear to you?
7. When the X-8R is reconnected: the response of …/api/ebx/x8r?ApiKey=….

Thanks again for your patience and precise readings!

Hi @lmilcent

We’re going to focus on the RT2 for now because unplugging/replugging devices in the electrical panel isn’t ideal and I have the TIC wire broken in this case, so since I’ve reset it, it will be easier to start from a clean config. I’ll see PM to change the TIC cable and then reconfigure the tores, etc. After that, I’ll provide you with the elements to move forward with the RT2, and once that’s okay, we’ll see about switching to the ED3, etc. Is that okay?

That’s perfect @cce66, we’ll do it like this: we’ll focus on the RT2 first, and we’ll pick up the ED3 once the RT2 is settled.

Take your time with the TIC cable and the reconfigured tores. Once that’s done, I’ll need for the RT2:

  • the API response of the RT2 object (like you did for the ED3, without your API key);
  • the names you give to the tores and the pilot wire zones;
  • a screenshot of the RT2 web page with the current powers, to compare with what Gladys displays.

I’ll check as soon as you post.

Good evening @lmilcent
While waiting for me to reinstall my IPX800V3
The relay control is working fine
However, to get the status of the inputs, you need to parse status.xml
For digital input 1, it’s
dn for connected
up for disconnected
It would be great to be able to set the polling frequency in ms for analog or digital inputs in the integration
If possible, pre-fill the device names as IPX800V3- to have IPX800V3-D1, IPX800V3-A1, IPX800V3-R1. It’s easier to update or integrate into the dashboard later
In the configuration UI, have the ability to set a range R1-R8 at this level (to control from R1 to R8)

However, ignore 01/01/2012
87:-109:07
I think there is a hardware issue with this point

http://192.168.1.235/status.xml
<response>
<led0>0</led0>
<led1>0</led1>
<led2>0</led2>
<led3>0</led3>
<led4>0</led4>
<led5>0</led5>
<led6>0</led6>
<led7>0</led7>
<led8>0</led8>
<led9>0</led9>
<led10>0</led10>
<led11>0</led11>
<led12>0</led12>
<led13>0</led13>
<led14>0</led14>
<led15>0</led15>
<led16>0</led16>
<led17>0</led17>
<led18>0</led18>
<led19>0</led19>
<led20>0</led20>
<led21>0</led21>
<led22>0</led22>
<led23>0</led23>
<led24>0</led24>
<led25>0</led25>
<led26>0</led26>
<led27>0</led27>
<led28>0</led28>
<led29>0</led29>
<led30>0</led30>
<led31>0</led31>

<btn0>up</btn0>
<btn1>up</btn1>
<btn2>up</btn2>
<btn3>up</btn3>
<btn4>up</btn4>
<btn5>up</btn5>
<btn6>up</btn6>
<btn7>up</btn7>
<btn8>up</btn8>
<btn9>up</btn9>
<btn10>up</btn10>
<btn11>up</btn11>
<btn12>up</btn12>
<btn13>up</btn13>
<btn14>up</btn14>
<btn15>up</btn15>
<btn16>up</btn16>
<btn17>up</btn17>
<btn18>up</btn18>
<btn19>up</btn19>
<btn20>up</btn20>
<btn21>up</btn21>
<btn22>up</btn22>
<btn23>up</btn23>
<btn24>up</btn24>
<btn25>up</btn25>
<btn26>up</btn26>
<btn27>up</btn27>
<btn28>up</btn28>
<btn29>up</btn29>
<btn30>up</btn30>
<btn31>up</btn31>


<day>01/01/2012 </day>
<time0>87:-109:07</time0> 

<analog0>0</analog0>
<analog1>0</analog1>
<analog2>0</analog2>
<analog3>0</analog3>
<analog4>0</analog4>
<analog5>0</analog5>
<analog6>0</analog6>
<analog7>0</analog7>
<analog8>0</analog8>
<analog9>0</analog9>
<analog10>0</analog10>
<analog11>0</analog11>
<analog12>0</analog12>
<analog13>0</analog13>
<analog14>0</analog14>
<analog15>0</analog15>


<anselect0>0</anselect0>
<anselect1>0</anselect1>
<anselect2>0</anselect2>
<anselect3>0</anselect3>
<anselect4>0</anselect4>
<anselect5>0</anselect5>
<anselect6>0</anselect6>
<anselect7>0</anselect7>
<anselect8>0</anselect8>
<anselect9>0</anselect9>
<anselect10>0</anselect10>
<anselect11>0</anselect11>
<anselect12>0</anselect12>
<anselect13>0</anselect13>
<anselect14>0</anselect14>
<anselect15>0</anselect15>

<count0>0</count0> 
<count1>0</count1> 
<count2>0</count2> 
<count3>0</count3> 
```<count4>0</count4> 
<count5>0</count5> 
<count6>0</count6> 
<count7>0</count7> 

<tinfo>---</tinfo>
<version>3.05.69</version>

</response>


Thanks @cce66 for your feedback and for the status.xml, it’s exactly what was needed. It’s in the v0.2.0: Release v0.2.0 · LM1LC3N7/gladys-ipx800-v3 · GitHub (the 0.2.1, published right after, contains the same code; it will be in the store at the next indexer run).

Inputs
The integration reads the digital inputs in status.xml, as you described: <btn0>dn</btn0> = connected, up = disconnected (btn0 = D1). Your status.xml (without the IP address) now serves as a test. <day> and <time0> are never read.
For analog inputs, A1 to A16 are read, but a device only appears for a sensor type published by GCE (2, 4, 5, or 6). In your case, they are all type 0: no analog device will appear for now.

Polling Frequency
New field « Read inputs every (milliseconds) », from 1000 to 300000. Only one request at a time, and the IPX rests at least as long as it took to respond. To return to the normal interval, type 0 (Gladys does not allow clearing a numeric field).
A partial shutdown always happens immediately, regardless of the pace.

Names
New devices are named IPX800V3-R1, IPX800V3-D1, IPX800V3-A1 (and IPX800V3-2-R1 for a second IPX). Those already created keep their name.

Relay Ranges
You can write R1-R8 (or R1-R8:light for lights) in the relay list. A reversed or range beyond R32 is entirely ignored, and a relay listed twice with a different type keeps the first (the integration state signals this).

I still don’t have an IPX800 V3: everything was tested on a fake IPX built from your status.xml. Let me know if the inputs come back to you and at what rate you set it. For the RT2, I’m available as soon as you’ve put the TIC cable back in.

Hi @lmilcent
I was able to rewire my TIC on the ecodevices RT2, let me know what you need.

For the ipx800v3 update, everything is fine for the update but a remark for “Options Read every (seconds)” 5s seems insufficient and it duplicates with a read on the digital inputs I find


when you click on save, there is no feedback that it is validated

Great job @cce66, thanks!

For the RT2, I would need:

  • the API response of the RT2 object, as you did for the ED3 (without your API key);
  • the names you give to the toroids and the pilot wire zones;
  • a screenshot of the RT2 web page with the current powers, to compare with what Gladys displays.

For the IPX800 V3, thanks for the feedback. You’re right, the two fields are redundant: when « Read inputs every (milliseconds) » is filled, the entire status page (including relays) is already read at that rate, and the field in seconds is no longer useful. I will merge them into a single setting in the next version, and I will let you know here upon release.

For the « Save » button without confirmation in the Devices tab: this page is part of Gladys, not the integration, so I can’t change it on my end.

@cce66 it’s in the v0.2.2: Release v0.2.2 · LM1LC3N7/gladys-ipx800-v3 · GitHub (it will arrive in the store at the next indexer run).

There is now only one setting, « Read every (milliseconds) », from 1000 to 300000: it controls the reading of the entire status page, including relays and inputs. The field in seconds has disappeared.

On update, nothing is lost: if the field in milliseconds was filled, it is kept (for you, 1000 ms); otherwise, the old setting in seconds is reused. Typing 0 reverts to this previous setting, or to 10 s.

Below 5000 ms, the IPX always rests at least as long as it took to respond, and only one request goes out at a time. A shutdown always happens immediately.

As before, tested only on a fake IPX built from your status.xml: let me know if the pace suits you.

Hi @lmilcent

For the RT2, here is http://192.168.1.231/admin/status.json
for the apikey, no problem, they are reinitialized for the setup in the table, that’s for testing :wink:

{
	"product": "EcoDevices RT2",
	"configmac": "68:27:19:XX:XX:XX",
	"configip": "192.168.1.231",
	"configport": "80",
	"infofirm": "3.00.04",
	"date": "14/11/2026",
	"heure": "12:22:26",
	"ioname10": "Relay 1",
	"ioname11": "Relay 2",
	"ioname18": "Relay 3",
	"ioname19": "Relay 4",
	"ioname110": "Relay 5",
	"ioname111": "Relay 6",
	"ioname112": "Relay 7",
	"ioname113": "Relay 8",
	"ioname114": "Relay 9",
	"ioname115": "Relay 10",
	"ioname00": "Input 1",
	"ioname01": "Input 2",
	"ioname02": "Input 3",
	"ioname03": "Input 4",
	"ioname08": "Input 5",
	"ioname09": "Input 6",
	"ioname010": "Input 7",
	"ioname011": "Input 8",
	"ioname012": "Input 9",
	"ioname013": "Input 10",
	"ioname014": "Input 11",
	"ioname015": "Input 12",
	"ioname30": "Counter 1",
	"ioname31": "Counter 2",
	"ioname32": "Counter 3",
	"ioname33": "Counter 4",
	"ioname34": "Counter 5",
	"ioname35": "Counter 6",
	"ioname36": "Counter 7",
	"ioname37": "Counter 8",
	"ioname38": "Counter 9",
	"ioname39": "Counter 10",
	"ioname310": "Counter 11",
	"ioname311": "Counter 12",
	"ioname50": "Power Counter 1",
	"ioname51": "Power Counter 2",
	"ioname52": "Power Counter 3",
	"ioname53": "Power Counter 4",
	"ioname54": "Power Counter 5",
	"ioname55": "Power Counter 6",
	"ioname56": "Power Counter 7",
	"ioname57": "Power Counter 8",
	"ioname58": "Power Counter 9",
	"ioname59": "Power Counter 10",
	"ioname510": "Power Counter 11",
	"ioname511": "Power Counter 12",
	"ioname512": "Power Counter 13",
	"ioname513": "Power Counter 14",
	"ioname514": "Power Counter 15",
	"ioname515": "Power Counter 16",
	"ioname516": "Power Counter 17",
	"ioname517": "Power Counter 18",
	"ioname518": "Power Counter 19",
	"ioname519": "Power Counter 20",
	"xths01": "0",
	"xths02": "0",
	"xths03": "0",
	"xths11": "0",
	"xths12": "0",
	"xths13": "0",
	"in": "000000000000",
	"rly": "0000000000",
	"rlyta": "0000000000",
	"vout": "00000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000",
	"voutta": "00000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000000",
	"eno": "000000000000000000000000",
	"enoA0": "0",
	"enoA1": "0",
	"enoA2": "0",
	"enoA3": "0",
	"enoA4": "0",
	"enoA5": "0",
	"enoA6": "0",
	"enoA7": "0",
	"enoA8": "0",
	"enoA9": "0",
	"enoA10": "0",
	"enoA11": "0",
	"enoA12": "0",
	"enoA13": "0",
	"enoA14": "0",
	"enoA15": "0",
	"enoA16": "0",
	"enoA17": "0",
	"enoA18": "0",
	"enoA19": "0",
	"enoA20": "0",
	"enoA21": "0",
	"enoA22": "0",
	"enoA23": "0",
	"x4fp10": "255",
	"x4fp11": "255",
	"x4fp12": "255",
	"x4fp13": "255",
	"x4fp14": "255",
	"x4fp20": "255",
	"x4fp21": "255",
	"x4fp22": "255",
	"x4fp23": "255",
	"x4fp24": "255",
	"etiquette0": "ADCO",
	"etiquette1": "OPTARIF",
	"etiquette2": "ISOUSC",
	"etiquette3": "BASE",
	"etiquette4": "HCHC",
	"etiquette5": "HCHP",
	"etiquette6": "EJPHN",
	"etiquette7": "EJPHPM",
	"etiquette8": "BBRHCJB",
	"etiquette9": "BBRHPJB",
	"etiquette10": "BBRHCJW",
	"etiquette11": "BBRHPJW",
	"etiquette12": "BBRHCJR",
	"etiquette13": "BBRHPJR",
	"etiquette14": "PEJP",
	"etiquette15": "PTEC",
	"etiquette16": "DEMAIN",
	"etiquette17": "IINST",
	"etiquette18": "IINST1",
	"etiquette19": "IINST2",
	"etiquette20": "IINST3",
	"etiquette21": "ADPS",
	"etiquette22": "IMAX",
	"etiquette23": "IMAX1",
	"etiquette24": "IMAX2",
	"etiquette25": "IMAX3",
	"etiquette26": "-",
	"etiquette27": "PAPP",
	"etiquette28": "HHPHC",
	"etiquette29": "-",
	"etiquette30": "-",
	"etiquette31": "-",
	"etiquetteVal0": "000000000000",
	"etiquetteVal1": "BASE",
	"etiquetteVal2": "45",
	"etiquetteVal3": "000000000",
	"etiquetteVal4": "",
	"etiquetteVal5": "",
	"etiquetteVal6": "",
	"etiquetteVal7": "",
	"etiquetteVal8": "",
	"etiquetteVal9": "",
	"etiquetteVal10": "",
	"etiquetteVal11": "",
	"etiquetteVal12": "",
	"etiquetteVal13": "",
	"etiquetteVal14": "",
	"etiquetteVal15": "TH..",
	"etiquetteVal16": "",
	"etiquetteVal17": "003",
	"etiquetteVal18": "",
	"etiquetteVal19": "",
	"etiquetteVal20": "",
	"etiquetteVal21": "",
	"etiquetteVal22": "053",
	"etiquetteVal23": "",
	"etiquetteVal24": "",
	"etiquetteVal25": "",
	"etiquetteVal26": "",
	"etiquetteVal27": "00680",
	"etiquetteVal28": "",
	"etiquetteVal29": "",
	"etiquetteVal30": "",
	"etiquetteVal31": "",
	"poste0": "Post 1",
	"info0": "0,0",
	"poste1": "Post 2",
	"info1": "0,0",
	"poste2": "Post 3",
	"info2": "0,0",
	"poste3": "Post 4",
	"info3": "0,0",
	"poste4": "Post 5",
	"info4": "0,0",
	"poste5": "Post 6",
	"info5": "0,0",
	"poste6": "Post 7",
	"info6": "0,0",
	"poste7": "Post 8",
	"info7": "0,0,0",
	"instant": "0,0,0,0,0,0,0,0",
	"ssposte00": "Sub-Post 1",
	"sspencours00": " ",
	"sspindex00": "--      ",
	"ssptoday00": "--      ",
	"ssposte01": "Sub-Post 2",
	"sspencours01": " ",
	"sspindex01": "--      ",
	"ssptoday01": "--      ",
	"ssposte02": "Sub-Post 3",
	"sspencours02": " ",
	"sspindex02": "--      ",
	"ssptoday02": "--      ",
	"ssposte03": "Sub-Post 4",
	"sspencours03": " ",
	"sspindex03": "--      ",
	"ssptoday03": "--      ",
	"ssposte04": "Sub-Post 5",
	"sspencours04": " ",
	"sspindex04": "--      ",
	"ssptoday04": "--      ",
	"ssposte05": "Sub-Post 6",
	"sspencours05": " ",
	"sspindex05": "--      ",
	"ssptoday05": "--      ",
	"ssposte06": "Sub-Post 7",
	"sspencours06": " ",
	"sspindex06": "--      ",
	"ssptoday06": "--      ",
	"ssposte07": "Sub-Post 8",
	"sspencours07": " ",
	"sspindex07": "--      ",
	"ssptoday07": "--      ",
	"ssposte10": "Sub-Post 1",
	"sspencours10": " ",
	"sspindex10": "--      ",
	"ssptoday10": "--      ",
	"ssposte11": "Sub-Post 2",
	"sspencours11": " ",
	"sspindex11": "--      ",
	"ssptoday11": "--      ",
	"ssposte12": "Sub-Post 3",
	"sspencours12": " ",
	"sspindex12": "--      ",
	"ssptoday12": "--      ",
	"ssposte13": "Sub-Post 4",
	"sspencours13": " ",
	"sspindex13": "--      ",
	"ssptoday13": "--      ",
	"ssposte14": "Sub-Post 5",
	"sspencours14": " ",
	"sspindex14": "--      ",
	"ssptoday14": "--      ",
	"ssposte15": "Sub-Post 6",
	"sspencours15": " ",
	"sspindex15": "--      ",
	"ssptoday15": "--      ",
	"ssposte16": "Sub-Post 7",
	"sspencours16": " ",
	"sspindex16": "--      ",
	"ssptoday16": "--      ",
	"ssposte17": "Sub-Post 8",
	"sspencours17": " ",
	"sspindex17": "--      ",
	"ssptoday17": "--      ",
	"ssposte20": "Sub-Post 1",
	"sspencours20": " ",
	"sspindex20": "--      ",
	"ssptoday20": "--      ",
	"ssposte21": "Sub-Post 2",
	"sspencours21": " ",
	"sspindex21": "--      ",
	"ssptoday21": "--      ",
	"ssposte22": "Sub-Post 3",
	"sspencours22": " ",
	"sspindex22": "--      ",
	"ssptoday22": "--      ",
	"ssposte23": "Sub-Post 4",
	"sspencours23": " ",
	"sspindex23": "--      ",
	"ssptoday23": "--      ",
	"ssposte24": "Sub-Post 5",
	"sspencours24": " ",
	"sspindex24": "--      ",
	"ssptoday24": "--      ",
	"ssposte25": "Sub-Post 6",
	"sspencours25": " ",
	"sspindex25": "--      ",
	"ssptoday25": "--      ",
	"ssposte26": "Sub-Post 7",
	"sspencours26": " ",
	"sspindex26": "--      ",
	"ssptoday26": "--      ",
	"ssposte27": "Sub-Post 8",
	"sspencours27": " ",
	"sspindex27": "--      ",
	"ssptoday27": "--      ",
	"ssposte30": "Sub-Post 1",
	"sspencours30": " ",
	"sspindex30": "--      ",
	"ssptoday30": "--      ",
	"ssposte31": "Sub-Post 2",
	"sspencours31": " ",
	"sspindex31": "--      ",
	"ssptoday31": "--      ",
	"ssposte32": "Sub-Post 3",
	"sspencours32": " ",
	"sspindex32": "--      ",
	"ssptoday32": "--      ",
	"ssposte33": "Sub-Post 4",
	"sspencours33": " ",
	"sspindex33": "--      ",
	"ssptoday33": "--      ",
	"ssposte34": "Sub-Post 5",
	"sspencours34": " ",
	"sspindex34": "--      ",
	"ssptoday34": "--      ",
	"ssposte35": "Sub-Post 6",
	"sspencours35": " ",
	"sspindex35": "--      ",
	"ssptoday35": "--      ",
	"ssposte36": "Sub-Post 7",
	"sspencours36": " ",
	"sspindex36": "--      ",
	"ssptoday36": "--      ",
	"ssposte37": "Sub-Post 8",
	"sspencours37": " ",
	"sspindex37": "--      ",
	"ssptoday37": "--      ",
	"ssposte40": "Sub-Post 1",
	"sspencours40": " ",
	"sspindex40": "--      ",
	"ssptoday40": "--      ",
	"ssposte41": "Sub-Post 2",
	"sspencours41": " ",
	"sspindex41": "--      ",
	"ssptoday41": "--      ",
	"ssposte42": "Sub-Post 3",
	"sspencours42": " ",
	"sspindex42": "--      ",
	"ssptoday42": "--      ",
	"ssposte43": "Sub-Post 4",
	"sspencours43": " ",
	"sspindex43": "--      ",
	"ssptoday43": "--      ",
	"ssposte44": "Sub-Post 5",
	"sspencours44": " ",
	"sspindex44": "--      ",
	"ssptoday44": "--      ",
	"ssposte45": "Sub-Post 6",
	"sspencours45": " ",
	"sspindex45": "--      ",
	"ssptoday45": "--      ",
	"ssposte46": "Sub-Post 7",
	"sspencours46": " ",
	"sspindex46": "--      ",
	"ssptoday46": "--      ",
	"ssposte47": "Sub-Post 8",
	"sspencours47": " ",
	"sspindex47": "--      ",
	"ssptoday47": "--      ",
	"ssposte50": "Sub-Post 1",
	"sspencours50": " ",
	"sspindex50": "--      ",
	"ssptoday50": "--      ",
	"ssposte51": "Sub-Post 2",
	"sspencours51": " ",
	"sspindex51": "--      ",
	"ssptoday51": "--      ",
	"ssposte52": "Sub-Post 3",
	"sspencours52": " ",
	"sspindex52": "--      ",
	"ssptoday52": "--      ",
	"ssposte53": "Sub-Post 4",
	"sspencours53": " ",
	"sspindex53": "--      ",
	"ssptoday53": "--      ",
	"ssposte54": "Sub-Post 5",
	"sspencours54": " ",
	"sspindex54": "--      ",
	"ssptoday54": "--      ",
	"ssposte55": "Sub-Post 6",
	"sspencours55": " ",
	"sspindex55": "--      ",
	"ssptoday55": "--      ",
	"ssposte56": "Sub-Post 7",
	"sspencours56": " ",
	"sspindex56": "--      ",
	"ssptoday56": "--      ",
	"ssposte57": "Sub-Post 8",
	"sspencours57": " ",
	"sspindex57": "--      ",
	"ssptoday57": "--      ",
	"ssposte60": "Sub-Post 1",
	"sspencours60": " ",
	"sspindex60": "--      ",
	"ssptoday60": "--      ",
	"ssposte61": "Sub-Post 2",
	"sspencours61": " ",
	"sspindex61": "--      ",
	"ssptoday61": "--      ",
	"ssposte62": "Sub-Post 3",
	"sspencours62": " ",
	"sspindex62": "--      ",
	"ssptoday62": "--      ",
	"ssposte63": "Sub-Post 4",
	"sspencours63": " ",
	"sspindex63": "--      ",
	"ssptoday63": "--      ",
	"ssposte64": "Sub-Post 5",
	"sspencours64": " ",
	"sspindex64": "--      ",
	"ssptoday64": "--      ",
	"ssposte65": "Sub-Post 6",
	"sspencours65": " ",
	"sspindex65": "--      ",
	"ssptoday65": "--      ",
	"ssposte66": "Sub-Post 7",
	"sspencours66": " ",
	"sspindex66": "--      ",
	"ssptoday66": "--      ",
	"ssposte67": "Sub-Post 8",
	"sspencours67": " ",
	"sspindex67": "--      ",
	"ssptoday67": "--      ",
	"ssposte70": "Sub-Post 1",
	"sspencours70": " ",
	"sspindex70": "--      ",
	"ssptoday70": "--      ",
	"ssposte71": "Sub-Post 2",
	"sspencours71": " ",
	"sspindex71": "--      ",
	"ssptoday71": "--      ",
	"ssposte72": "Sub-Post 3",
	"sspencours72": " ",
	"sspindex72": "--      ",
	"ssptoday72": "--      ",
	"ssposte73": "Sub-Post 4",
	"sspencours73": " ",
	"sspindex73": "--      ",
	"ssptoday73": "--      ",
	"ssposte74": "Sub-Post 5",
	"sspencours74": " ",
	"sspindex74": "--      ",
	"ssptoday74": "--      ",
	"ssposte75": "Sub-Post 6",
	"sspencours75": " ",
	"sspindex75": "--      ",
	"ssptoday75": "--      ",
	"ssposte76": "Sub-Post 7",
	"sspencours76": " ",
	"sspindex76": "--      ",
	"ssptoday76": "--      ",
	"ssposte77": "Sub-Post 8",
	"sspencours77": " ",
	"sspindex77": "--      ",
	"ssptoday77": "--      ",
	"trade": "111111111",
	"mois": "0,0,0,0,0,0,0,0,0,0,0,0",
	"vref": "0.00",
	"vmesure": "233.60",
	"gsmco": "0",
	"gsmnetwork": "",
	"gsmpin": "",
	"ddnsstate": "Unknown - The Dynamic DNS client is pending an update.",
	"periodeencours": "TH..",
	"prixcourant30": "--      ",
	"prixcourant31": "--      ",
	"prixcourant32": "--      ",
	"prixcourant33": "--      ",
	"prixcourant34": "--      ",
	"prixcourant35": "--      ",
	"prixcourant36": "--      ",
	"prixcourant37": "--      ",
	"prixcourant38": "--      ",
	"prixcourant39": "--      ",
	"prixcourant310": "--      ",
	"prixcourant311": "--      ",
	"indexcourant30": "--      ",
	"indexcourant31": "--      ",
	"indexcourant32": "--      ",
	"indexcourant33": "--      ",
	"indexcourant34": "--      ",
	"indexcourant35": "--      ",
	"indexcourant36": "--      ",
	"indexcourant37": "--      ",
	"indexcourant38": "--      ",
	"indexcourant39": "--      ",
	"indexcourant310": "--      ",
	"indexcourant311": "--      ",
	"indexcourant50": "--      ",
	"indexcourant51": "--      ",
	"indexcourant52": "--      ",
	"indexcourant53": "--      ",
	"indexcourant54": "--      ",
	"indexcourant55": "--      ",
	"indexcourant56": "--      ",
	"indexcourant57": "--      ",
	"indexcourant58": "--      ",
	"indexcourant59": "--      ",
	"indexcourant510": "--      ",
	"indexcourant511": "--      ",
	"indexcourant512": "--      ",
	"indexcourant513": "--      ",
	"indexcourant514": "--      ",
	"indexcourant515": "--      ",
	"indexcourant516": "--      ",
	"indexcourant517": "--      ",
	"indexcourant518": "--      ",
	"indexcourant519": "--      ",
	"prixcourant50": "--      ",
	"prixcourant51": "--      ",
	"prixcourant52": "--      ",
	"prixcourant53": "--      ",
	"prixcourant54": "--      ",
	"prixcourant55": "--      ",
	"prixcourant56": "--      ",
	"prixcourant57": "--      ",
	"prixcourant58": "--      ",
	"prixcourant59": "--      ",
	"prixcourant510": "--      ",
	"prixcourant511": "--      ",
	"prixcourant512": "--      ",
	"prixcourant513": "--      ",
	"prixcourant514": "--      ",
	"prixcourant515": "--      ",
	"prixcourant516": "--      ",
	"prixcourant517": "--      ",
	"prixcourant518": "--      ",
	"prixcourant519": "--      ",
	"prixcourant640": "7.15",
	"prixcourant641": "--      ",
	"prixcourant642": "--      ",
	"prixcourant643": "--      ",
	"prixcourant644": "--      ",
	"prixcourant645": "--      ",
	"prixcourant646": "--      ",
	"indexcourant640": "132833958",
	"indexcourant641": "--      ",
	"indexcourant642": "--      ",
	"indexcourant643": "--      ",
	"indexcourant644": "--      ",
	"indexcourant645": "--      ",
	"indexcourant646": "--      ",
	"valeurfacteurpuissance1": "-",
	"valeurfacteurpuissance2": "-",
	"valeurfacteurpuissance3": "-",
	"valeurfacteurpuissance4": "-"
}

Thanks @cce66 for the RT2 status.json!

I added it to the RT2 integration tests (without the MAC or your index). Good news: nothing to fix. The integration reads the /api/xdevices.json API, which your 3.00.04 firmware already serves, and the values match. Your 11/14 teleinfo index (≈ 132,834 kWh) follows the 10/31 one, about 21 kWh per day, which matches your 680 VA.

What Gladys displays today with this box (v0.1.4):

  • relays 1 to 10 and inputs 1 to 12;
  • the teleinfo 1 index, in kWh;
  • the pulse counters only when they have a value (“–” remains unknown, never 0);
  • the pilot zones: no mode read as long as no X-4FP is connected (255 everywhere at your place).

Not yet read: the instantaneous power, the tariff period (TH..), the voltage, and the posts. That’s the next step. To do it according to your box rather than the documentation, can you send me the responses to these two addresses (removing your key)?

  • http://192.168.1.231/api/xdevices.json?key=YOUR_KEY&Get=TI
  • http://192.168.1.231/api/xdevices.json?key=YOUR_KEY&Get=P

By the way, your BASE is at 0 while the index is advancing: this is normal with a Linky in standard mode, which does not fill the historical labels.

hi @lmilcent

here are the 2 requests and I have a Sagem SC10 meter so no Linky

http://192.168.1.231/api/xdevices.json?key=TA_CLE&Get=TI
{
    "product": "EcoDevices_RT",
    "status": "Success",
    "ADCO": "0xxxxxxxxxxxx",
    "OPTARIF": "BASE",
    "ISOUSC": "45",
    "BASE": "132852908",
    "PTEC": "TH..",
    "IINST": "004",
    "IMAX": "053",
    "PAPP": "00870"
}
http://192.168.1.231/api/xdevices.json?key=TA_CLE&Get=P
{
    "product": "EcoDevices_RT",
    "status": "Success",
    "INSTANT_POSTE1": 0,
    "INSTANT_POSTE2": 0,
    "INSTANT_POSTE3": 0,
    "INSTANT_POSTE4": 0,
    "INSTANT_POSTE5": 0,
    "INSTANT_POSTE6": 0,
    "INSTANT_POSTE7": 0,
    "INSTANT_POSTE8": 0
}